IMO, who ever gigged it is missing something.
The restriction on grounding with flex in 250.118 means that in most transformer situations the flex not a ground so bonding bushings or equivalent to bonding PVC
If you have a piece of FMC over six feet or used on a circuit greater than twenty amps you pull a green in it, so a bond bushing does nothing to make anything better or safer. It doesn't matter if it is for lights in a ceiling or a 75kva transformer.......What about FMC and LFMC? The M of course stands for metal, which would mean it would need to be bonded.
Liquidtite can be used as an equipment ground up to sixty amps for sizes 3/4 up to 1 1/4. The wire acts as a shorting conductor across the coils so the metal functions as an equipment ground when ground fault current hits it.Are some LFMC types better at carrying a bond than other types? Like the kind with the embedded ground wire in the metal coils?
It gets even better.
He made my buddy phase every conductor except the grounds,,,,,purple, then phase on top of purple , the trade colors. The neutrals are black- phased purple and grey. All the branch circuits are purple thhn then, brown A orange B and yellow C..
I think there's a power struggle amist.
The same inspector wants all branch circuits to begin and end in their respective phase color.
I really have no problem with his over doing it but try putting in the bid a price for phasing every thing purple then another phase on top but its not a NEC requirement.
I suspect he would tell you that he is just asking for "common sense" requirements. That is a problem because it is subjective. I would rather he stick to enforcing the codeI would fight this guy to the ends of the earth. We would not get along. I cannot stand those inspectors that pull the AHJ card without code or at least some common sense to back it up.
I agree, he is just eating up our time with non sense.I suspect he would tell you that he is just asking for "common sense" requirements. That is a problem because it is subjective. I would rather he stick to enforcing the code
I suspect he would tell you that he is just asking for "common sense" requirements. That is a problem because it is subjective. I would rather he stick to enforcing the code
I thought the rule is that any citation by an inspector, has to be based on a specific code requirement.
The only place where an inspector's own interpretation would be allowed, would be in cases where the code is subject to interpretation.
Since the FMC is being used to provide flexibility a wire type EGC is required, also FMC is not permitted to serve as a SSBJ. The use of a bonding bushing on a flexible raceway which does not qualify as an EGC or as a SSBJ seems silly and as Augie stated akin to putting them on PVC.
The fact a raceway is not in itself an EGC does not mean the raceway itself does not require bonding.
Consider that FMC is an allowed service raceway. 230.43(15)
Do we have to bond it?
It's metal so of course yes, but the FMC is bonded by the use of a listed FMC connector a separate bonding bushing is not required.