Wayne you and I differ on 300.4, IMO any raceway that connects to a enclosure with 4 AWG or larger requires a bushing.Originally posted by hurk27:
300.4 is only required where a raceway enters a enclosure. A fitting for FMC is not a raceway. The only raceway to me that would enter an enclosure would be of the threaded types.
Bob300.4(F) Insulated Fittings. Where raceways containing ungrounded conductors 4 AWG or larger enter a cabinet, box enclosure, or raceway, the conductors shall be protected by a substantial fitting providing a smoothly rounded insulating surface, unless the conductors are separated from the fitting or raceway by substantial insulating material that is securely fastened in place.
Exception: Where threaded hubs or bosses that are an integral part of a cabinet, box enclosure, or raceway provide a smoothly rounded or flared entry for conductors.
Conduit bushings constructed wholly of insulating material shall not be used to secure a fitting or raceway. The insulating fitting or insulating material shall have a temperature rating not less than the insulation temperature rating of the installed conductors.
I agree it need's one because of the vibration from a transformer, but most fittings I have seen have a well rounded throat? As Dave (Websparky) has said it is a poorly written section.iwire
Member
Member # 47
posted October 20, 2004 06:22 PM
--------------------------------------------------------------------------------
quote:
--------------------------------------------------------------------------------
When did the NEC start requiring an "Insulated" bushing to be installed on a SE cable fitting.?
--------------------------------------------------------------------------------
They haven't, the requirement is for raceways only.
No, same view.Originally posted by hurk27:
Bob you must have changed your view on this as you posted this when I had this question back in October :
I agree it need's one because of the vibration from a transformer, but most fittings I have seen have a well rounded throat? As Dave (Websparky) has said it is a poorly written section.iwire
Member
Member # 47
posted October 20, 2004 06:22 PM
--------------------------------------------------------------------------------
quote:
--------------------------------------------------------------------------------
When did the NEC start requiring an "Insulated" bushing to be installed on a SE cable fitting.?
--------------------------------------------------------------------------------
They haven't, the requirement is for raceways only.
I can't think of a hub or a boss that would be a part of a raceway?Where threaded hubs or bosses that are an integral part of a cabinet, box enclosure, or raceway provide a smoothly rounded or flared entry for conductors.