Here's my bonding bushing requirement checklist. Anyone want to add to it?
You need a bonding bushing if:
1. Your raceway contains service conductors.
2. Your raceway contains grounding electrode conductors. In fact, you may need one on both ends, for GEC performance. Is there a practical "short length" below which standard conduit bonding practices are acceptable in this application?
3. Your raceway terminates on non-metallic enclosures
4. Your raceway terminates on ring knockouts remaining, and the circuit exceeds 250 V to ground nominal
5. Your raceway does not terminate on an enclosure.
You do not need a bonding bushing if:
1. Your raceway is non-metallic.
2. The other end of your raceway terminates on another enclosure with proper electrical continuity to the raceway. Except where needed for GEC performance.
3. You use alternative fittings, such as a bonding locknut, a bonding Myers hub, with a screw to connect the EGC. Or other listed bonding fittings, which can receive a jumper.
4. In any of the above examples, a standard plastic bushing is an acceptable alternative
You need a bonding bushing if:
1. Your raceway contains service conductors.
2. Your raceway contains grounding electrode conductors. In fact, you may need one on both ends, for GEC performance. Is there a practical "short length" below which standard conduit bonding practices are acceptable in this application?
3. Your raceway terminates on non-metallic enclosures
4. Your raceway terminates on ring knockouts remaining, and the circuit exceeds 250 V to ground nominal
5. Your raceway does not terminate on an enclosure.
You do not need a bonding bushing if:
1. Your raceway is non-metallic.
2. The other end of your raceway terminates on another enclosure with proper electrical continuity to the raceway. Except where needed for GEC performance.
3. You use alternative fittings, such as a bonding locknut, a bonding Myers hub, with a screw to connect the EGC. Or other listed bonding fittings, which can receive a jumper.
4. In any of the above examples, a standard plastic bushing is an acceptable alternative