Are bonding bushings required when running a GEC to building steel if the conduit is EMT? Coming out of MDP ground bar to building steel. I know the answer but once again foreman is non compliant.
roger said:Bond bushings are not required, but both ends of the conduit must be bonded to the conductor by some means. At the panel it can simply be a connector and locknut, the other end could be a bond bushing or other means.
joeyww12000 said:Are bonding bushings required when running a GEC to building steel if the conduit is EMT? Coming out of MDP ground bar to building steel. I know the answer but once again foreman is non compliant.
dnem said:Roger: "At the panel it can simply be a connector and locknut"
250.92(B): "Standard locknuts or bushings shall not be the sole means for the bonding required by this section."
(B) Method of Bonding at the Service Electrical continuity at service equipment, service raceways, and service conductor enclosures shall be ensured by one of the following methods:
Service Conductors. The conductors from the service point to the service disconnecting means.
Service Point. The point of connection between the facilities of the serving utility and the premises wiring.
roger said:BTW, I can see where you are coming from but, if we use the reasoning that since this raceway is connected to the service equipment and must use more than a standard locknut for bonding, then we would have to use the same reasoning for any branch circuit conduit that enters a Main Panel as well.
Roger
dnem said:#1] What does the wording in the NEC actually say ? . Is it clear ? . If yes, then skip to #4.
#2] Is there other language within the NEC that might not directly apply but can help understand a word or phrase ? . If yes, then skip to #4.
#3] Is there info in an ROP, NEC Handbook, or UL Whitebook that helps clear up the question ?
#4] Take the best answer you have at this point and apply common sense to the specific installation that you're looking at.
#5] Is it still unclear which of several options are required ? . Then accept any of those possible options that the contractor chooses.
infinity said:I agree with Roger and have taken issue with Mike's graphic in the past because IMO it's incorrect.
dnem said:But we've been talking about 250.92(B): "Standard locknuts or bushings shall not be the sole means for the bonding required by this section."
Mike Holts graphic depicts 250.64(E). . How does the Mike Holt graphic misrepresent 250.64(E) ?
Bond bushings are not required, but both ends of the conduit must be bonded to the conductor by some means. At the panel it can simply be a connector and locknut, the other end could be a bond bushing or other means.
infinity said:I am in agreement with Roger's statement:
If you look at Mike's graphic it clearly shows the panel with a bonding bushing and jumper from the conduit to the neutral. This is not required since the neutral is bonded to the can and so is the conduit. The bonding jumper in this case is redundant and not required.
elohr46 said:However, the first sentence in that article (2005 codebook) says the "ferrous metal enclosure shall be securely fastened to the ground clamp or fitting".
Yes for bond bushings or yes it must be bonded at each end?wawireguy said:Required.. yes..
How do you know what will happen during a HV surge or a Lightning event with or without this bonding?wawireguy said:will anyone get hurt if they aren't there. No.