Bonding Bushing

Status
Not open for further replies.

kornbln

Senior Member
1) How is the grounding conductor for a bonding bushing sized?

2) Assuming the raceway with the bonding bushing contains a grounding wire of the appropriate size, is it acceptable to attach it to the bonding bushing before it lands on the grounding bar? Or does the bushing need a separate wire?
 
1) How is the grounding conductor for a bonding bushing sized??
depends..service {250.102(C)}, (250.66) or feeder/brach circuit {250.102(D)}.(250.122)

2) Assuming the raceway with the bonding bushing contains a grounding wire of the appropriate size, is it acceptable to attach it to the bonding bushing before it lands on the grounding bar? Or does the bushing need a separate wire?

It can be the conduit conductor
 