If concentric or eccentric ko's are used it depends on listing of the enclosure with such ko's. otherwise if listed for purpose or a same size opening as the raceway no additional bonding methods are required. See 250.97
If I remember correctly the exclusion of the bonding jumper for items listed for bonding over 250 volt to ground only applies to boxes. It would not apply to a disconnect switch or a panel enclosure, etc.
I think the ko's typically found on meter sockets are the heavier duty type listed for grounding over 250, but I have never dug into the paperwork to confirm.Copied from 2014 NEC:
"Exception: Where oversized, concentric, or eccentric knockouts are not encountered, or where a box or enclosure with concentric or eccentric knockouts is listed to provide a reliable bonding connection, the following methods shall be permitted:"
In a meter socket it is moot as you need to comply with 250.92 bonding.I think the ko's typically found on meter sockets are the heavier duty type listed for grounding over 250, but I have never dug into the paperwork to confirm.
In a meter socket it is moot as you need to comply with 250.92 bonding.
I think the ko's typically found on meter sockets are the heavier duty type listed for grounding over 250, but I have never dug into the paperwork to confirm.
yes good point, often true. Although there are meter packs with disconnects and cold sequenced metering.In a meter socket it is moot as you need to comply with 250.92 bonding.
No I am not sure, I have never dug into it. I believe it has been mentioned on here that the typical 4 sq box has ko's listed for >250 bonding also.Do you have any examples of what to look for on a datasheet, to determine if the ring KO's are rated for 250V-600V bonding? Not necessarily for a meter socket, just in general.
I have never seen anything approved other than junction boxes like 4 square.Do you have any examples of what to look for on a datasheet, to determine if the ring KO's are rated for 250V-600V bonding? Not necessarily for a meter socket, just in general.
My comment about meter sockets was a total assumption, I could very well be wrong. It just seems like those ko's are much tougher than anything else. Wish they were all like that, or better yet, things had no concentrics /eccentrics at all.I have never seen anything approved other than junction boxes like 4 square.
Would they even need to be? A raceway with SEC's would still require a bonding bushing regardless of the listing of the meter enclosure with concentric or eccentric KO's.I think the ko's typically found on meter sockets are the heavier duty type listed for grounding over 250, but I have never dug into the paperwork to confirm.
See posts 7,8,10Would they even need to be? A raceway with SEC's would still require a bonding bushing regardless of the listing of the meter enclosure with concentric or eccentric KO's.
That sums it up.See posts 7,8,10![]()