Are bonding bushings required from the main switch gear to a MDC 3' away? .................................................
Not enough information in you question. Voltage? Types of KO's?Are bonding bushings required from the main switch gear to a MDC 3' away? .................................................
Main distribution something?What is a MDC?
Is it really only for circuits over 250V? I was always told it was for all concentric knockouts, which made sense to me to ensure electrical continuity in case the pipe broke one of the remaining concentric rings of the KO and thus bonding continuity.
Is it really only for circuits over 250V? I was always told it was for all concentric knockouts, which made sense to me to ensure electrical continuity in case the pipe broke one of the remaining concentric rings of the KO and thus bonding continuity.
Concentric KO's are approved for bonding under 250 volts to ground. Some are even approved for over 250 volts to ground.Is it really only for circuits over 250V? I was always told it was for all concentric knockouts, which made sense to me to ensure electrical continuity in case the pipe broke one of the remaining concentric rings of the KO and thus bonding continuity.
Oh, I'm aware. This isn't the first time something I learned from another electrician turned out to be BS, lol.As more time marches on, you will be surprised at how much of the stuff you were told was BS.
Code aside, I do hate concentric/eccentric KO's and almost always get rid of them all and use reducing washers and use a BB if its a metal raceway. Those heavier duty KO's you typically find on meter sockets are ok and Ill typicall skip the RW, but since that is usually a service, you will need a BB anyway.Oh, I'm aware. This isn't the first time something I learned from another electrician turned out to be BS, lol.
That's part of why I decided to enroll in night classes and purchase a copy of the NEC for myself.
It just made sense to me so I never questioned this particular one because a bonding bushing with a jumper would ensure electrical continuity if the remaining concentric ever broke, for whatever reason.
Perhaps not NEC required and going a little "above and beyond," but the logic still seems sound.
sorry MDPWhat is a MDC?
1200a, 208vac, 3" KO'sNot enough information in you question. Voltage? Types of KO's?
No bonding bushngs required.1200a, 208vac, 3" KO's