When is it reguired to install a bonding bushing? I have been on many job sites and have noticed locations I feel would require one when there is one. Any help with the NEC article would be great!
27hillcrest said:When is it reguired to install a bonding bushing? I have been on many job sites and have noticed locations I feel would require one when there is one. Any help with the NEC article would be great!
27hillcrest said:Here is a location I assume that would need them a 225kva XFMR 480volt 208/120 being fed with a 4" flex 90 degree. The load side is 3 3" 90 degree flex connectors. Thanks,
You don't need a bonding bushing, but you do need a bonding jumper around the flex.Here is a location I assume that would need them a 225kva XFMR 480volt 208/120 being fed with a 4" flex 90 degree. The load side is 3 3" 90 degree flex connectors. Thanks,