Re: bonding bushings
twist:
a quick note added to what bob said, most, if not all, of your standard boxes (4" sq, etc) have eccentric knockouts now and the boxes are listed for grounding so its not as big an issue as it once was.
in more direct answer to your question. , IMHO, yes. That EGC you pull does not necessarily ground the raceway itself. If you are dealing with >250v, and the raceway terminates in concentric k.os, not in an approved grounded on both ends, then, yes, you must address bonding the conduit by an approved means.