bonding bushings

Status
Not open for further replies.

patl

Member
I am coming out of a 1600 amp 3ph 120/208 fused switch feeding a bank of 1ph meter with 4 sets of 500 mcm in 3 1/2" EMT. The AHJ wants me to use bonding bushings on the EMT run & pull a 4/0 ground in one of the coduits. Is this correct, i have never used bonding bushings on a fused run before and never had a problem.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: bonding bushings

No, the NEC does not require bonding bushings on this feeder.

The NEC does not require an EGC run in EMT.

If you decide to run an EGC it would be a violation to only run it in one of the raceways.

If you choose to run an EGC with parallel conductors you must run an EGC in each.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: bonding bushings

Is this feeder fused at 1600 amps? If so, he should have a problem with the 4 sets of 500MCM.
 

vanwalker

Senior Member
Location
lancaster
Re: bonding bushings

would protection of cable be an issue?(ampacity of feeders) please list code articles only, for interpetation issues.THANK YOU GEO
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: bonding bushings

Originally posted by vanwalker:
would protection of cable be an issue?(ampacity of feeders) please list code articles only, for interpetation issues.THANK YOU GEO
I am not following you. :confused:

The 4 sets of 500 kcmil are only good for 1520 amps, you can not move up to the next standard size OCP at this level. you would have to use a 1,200 OCP or run 4 sets of 600 Kcmil
 

dillon3c

Senior Member
Re: bonding bushings

Vanwalker,
As iwire and infinity have stated.

500kcmils-Table 310.16 @75 degree C column(copper).
380 amperes x 4=1520 amperes
*see 240.4 Protection of Conductors

240.4(B)(3)Quote:The next higher standard rating selected does not exceed 800 amperes.

240.4(C)Devices Rated Over 800 Amperes.
Quote:Where the overcurrent device is rated over 800 amperes,the ampacity of the conductors it protects shall be equal to or greater than the rating of the overcurrent device defined in 240.6

240.6 Standard Ampere Ratings.

240.6(A)Fuses and Fixed-Trip Circuit Breakers.

(you ask for code referances)
 

charlie

Senior Member
Location
Indianapolis
Re: bonding bushings

The reason four sets of 500 kcmil can't be used with a 1600 ampere overcurrent device is that the overcurrent device uses the conductor for a heat sink. The wire itself will not have a problem and the conductor damage curves show that. :D
 