300.4(G) Insulated Fittings. Where raceways contain 4 AWG
or larger insulated circuit conductors and these conductors
enter a cabinet, box, enclosure, or raceway, the conductors
shall be protected by a substantial fitting providing a
smoothly rounded insulating surface, unless the conductors
are separated from the fitting or raceway by substantial
insulating material that is securely fastened in place.
Exception: Where threaded hubs or bosses that are an integral
part of a cabinet, box, enclosure, or raceway provide
a smoothly rounded or flared entry for conductors.
Conduit bushings constructed wholly of insulating material
shall not be used to secure a fitting or raceway. The
insulating fitting or insulating material shall have a temperature
rating not less than the insulation temperature rating
of the installed conductors.