If armoured cable is run into an Pole light with a bond screw, does the cable in the pole require a connector to be bonded to an enclosure if already bonded from it's source?
Are you talking about type "AC cable"?
If so the sheath is the equipment grounding conductor and it pretty much needs to have a fitting on the end of the cable to bond to the enclosure it attaches to. In the somewhat rare case of not installing a fitting into an enclosure I suppose it may be acceptable to still put a connector on end of cable and install a grounding busing on the fitting so you can put a bonding jumper from there to wherever necessary.
Next question, if I understand correctly, is what circumstances do you have where running AC cable to a light pole is acceptable? Most instances it probably wouldn't be allowed because the pole is in a damp or wet location as well as methods required to get to the pole.
TEK isn't an NEC recognized cable type, but FWIW there are no cable types I'm aware of that don't require a connector of some sort at each end. :happyyes:
I believe the sheath must be bonded at both ends as a matter of continuity of the grounding path. Others may debate that bonding one end complies, but I say "path" implies "through" rather than just "from" or "to".
The bare grounding conductor within the cable is not in contact with the armor sheath. Thus bonding of the sheath relies on using a connector at each end.The CSA reference is TECK90...
Is this bare bond conductor a supplemental component designed to improve resistance of the sheath or is it a stand alone equipment grounding conductor? If it is there to improve resistance of the sheath then the bond wire plus the sheath together are the equipment grounding conductor - at least in a NEC covered AC or MC cable.The CSA reference is TECK90 which are Copper conductors in direct burial armored cable, and ACWU90 for aluminum in direct burial cable with armor.
In this installation, TECK90 is stubbed up into the Light Post and strapped from below. The armored sheath is bonded at the source, but the installer felt a connector and bonding bushing were not necessary, as the bare bond conductor inside was connected to an Lug inside the Post.
Interesting install was the Teck90 Service Cable that had the bare bond wire cut off at the Utility's connection end since it was inside of an PVC Weather head as an Inspector suggested, and apparently done in Industrial applications. I had thought the bare bond would be wrapped around the sheath... but would that cause sheath currents from bare conductor to the sheath?
Is this bare bond conductor a supplemental component designed to improve resistance of the sheath or is it a stand alone equipment grounding conductor? If it is there to improve resistance of the sheath then the bond wire plus the sheath together are the equipment grounding conductor - at least in a NEC covered AC or MC cable.
The bare grounding conductor within the cable is not in contact with the armor sheath. Thus bonding of the sheath relies on using a connector at each end.
I do not know whether CEC requires pass-through bonding or just dead-end bonding, but as I said earlier, all cables require a connector at each end.
Pass-through bonding is my terminology. It simply means a long conductive item such as sheathing or conduit is bonded on both ends so ground fault current originating at any location can pass through it. The contrary position is dead-end bonding, or bonding one end. Ground fault current from any external source may not pass through this conductive item if it is only bonded at one end.May I ask what you mean by "pass through bonding"? I recall being told bonding is to be done on both ends of the Cable in school, but was searching for our CEC code reference to it. Is it an NEC requirement to bond both ends because it is your bonding for all cables?