So I'm doing a case study on a project we are doing at work just for my own enjoyment.
We are bringing a 400amp 120/208 feeder into a can from a overhead drop with no EGC. From that can we are tapping to two 200amp panels. Should the can be bonded to the neutral? This is a outside temp FYI. We are using PVC conduit for the taps to the sub panels.
Now what if we had went with EMT conduit? The can would be bonded to the sub panels.
I decided the no ground with the feeders was fine, 250.32(B)
Also decided the taps were alright, 240.21(B)(5)
Can't find where it discusses bonding that can though. I know it needs to be bonded to the grounded conductor but want to see the code reference.