Bonding across hinged doors – Nema 4X Junction boxes and Control Panels, etc, CID2, (24VDC and 120VAC). Its industry practice to do this since the hinge is usually not considered to be a sufficient bond but there doesn't seem to be a NEC article that directly talks to this. I would say 501.30 and 250.96 are sufficient arguments in favor of, but our 'friends' in Construction aren't convinced. Any suggestions?
 

nhee2

Senior Member
Location
NH
I've always assumed this bond is a UL508 requirement and not NEC, independent of haz area requirements.
 

Jim1959

Senior Member
Location
Longmont, CO
As I worked in the trade, I always understood it to be required when there was an electrical device mounted in the door. It's obviously a good practice, especially View attachment HOFFMAN CSD INSTRUCTIONS.pdf in a classified area. I attached a sheet from the Hoffman CSD installation instructions. Just pictures, so there's not much info, but since they show it being bonded, I would say that it is required by the manufacturer and therefore by 110.3 B.
 

Dale001289

Senior Member
Location
Georgia
As I worked in the trade, I always understood it to be required when there was an electrical device mounted in the door. It's obviously a good practice, especially View attachment 18307 in a classified area. I attached a sheet from the Hoffman CSD installation instructions. Just pictures, so there's not much info, but since they show it being bonded, I would say that it is required by the manufacturer and therefore by 110.3 B.

good feedback, I will definitely use this as part of my response. Thanks!
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
UL 508a says this.

66.3.4 An internal bonding conductor shall be provided between a metal cover or a door on which
electrical components are mounted, and the enclosure or the equipment grounding terminal. The bonding
conductor shall have an ampacity not less than the largest circuit conductor used to connect the cover or
door-mounted components.
Exception: When all electrical components mounted to a metal cover or door are connected to a control
circuit rated 30V rms or less the bonding conductor is not required.

HOWEVER, this is in the section that only applies to control panels for industrial machines.

At one time, UL listed at least some Hoffman enclosures that had continuous SS hinge pins for the doors as being bonded without the need for a conductor being added. I don't know if that is the case anymore.

Generally if there might be a need for door bonding the enclosure manufacturer will provide studs for that purpose. I don't know that the absence or presence of them is meaningful though.
 

Dale001289

Senior Member
Location
Georgia
UL 508a says this.



HOWEVER, this is in the section that only applies to control panels for industrial machines.

At one time, UL listed at least some Hoffman enclosures that had continuous SS hinge pins for the doors as being bonded without the need for a conductor being added. I don't know if that is the case anymore.

Generally if there might be a need for door bonding the enclosure manufacturer will provide studs for that purpose. I don't know that the absence or presence of them is meaningful though.

Ok I will check into - thanks
 

Dale001289

Senior Member
Location
Georgia
As I worked in the trade, I always understood it to be required when there was an electrical device mounted in the door. It's obviously a good practice, especially View attachment 18307 in a classified area. I attached a sheet from the Hoffman CSD installation instructions. Just pictures, so there's not much info, but since they show it being bonded, I would say that it is required by the manufacturer and therefore by 110.3 B.

Spoke to Hoffman last night; they will not commit to saying hinges are electrically continuous and refer back to NEC for interpretation - imagine that.
I'm wondering if a simple resistance test between the two areas (i.e. door and enclosure) would show a significant difference in potential?
Since you've worked in trades, have you ever done this before?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Spoke to Hoffman last night; they will not commit to saying hinges are electrically continuous and refer back to NEC for interpretation - imagine that.
I'm wondering if a simple resistance test between the two areas (i.e. door and enclosure) would show a significant difference in potential?
Since you've worked in trades, have you ever done this before?

I suspect that UL has stopped listing the CH as being a bonding means since Hoffman now puts bonding studs in all their boxes.
 