A 500 kva transformer feeds a 120/ 208 power distribution cabinet. Three 4 inch conduits run between the transformer secondary cabinet and the power cabinet with a 1200 amp main. They are stubbed up on both ends with bonding bushings. There is also a single 4 inch conduit in the primary cabinet on the transformerwith a bonding bushing as well. The inspector is claiming the 3/0 bonding conductor joining the bushings in the transformer is too small. He is using table 250.66. I went by table 250.122 and used 3/0 as a bonding conductor on both ends of the stub ups. Any thought? Thanks