Bonding conduit

Status
Not open for further replies.
I am wanting to know if I need to bond my 3/4 inch conduit.

The only wire in it is a 1/0 ground. There are no current carrying conductors in the conduit.
It is the grounding system for a 400 amp service in a commercial building.

The purpose of the conduit is to protect the ground wire from abuse as it is in an unsecured area subject to potential vandalism.
 
If the conduit containing the GEC is ferrous metal then yes you must bond the conduit to the GEC.

See 250.64(E) for the fine details

When you run a single isolated conductor in a ferrous conduit and then apply a strong current to the conductor as would happen during a fault the combination of the single conductor and ferrous conduit raises the imdeance of the circuit.

By bonding the conduit to the GEC at each end you make the conduit and conductor act as a single conductor.
 
If the conduit containing the GEC is ferrous metal then yes you must bond the conduit to the GEC.

See 250.64(E) for the fine details

When you run a single isolated conductor in a ferrous conduit and then apply a strong current to the conductor as would happen during a fault the combination of the single conductor and ferrous conduit raises the imdeance of the circuit.

By bonding the conduit to the GEC at each end you make the conduit and conductor act as a single conductor.


What if it is metallic conduit, but non-ferrous, like aluminum conduit?
 
Bonding the Al conduit would lower the impedance, due to lightning is high frequency and tends to travel on the skin of the conductor. Information on why we bond metallic conduits for a GEC is in the IEE Green Book
 
Bonding the Al conduit would lower the impedance, due to lightning is high frequency and tends to travel on the skin of the conductor. Information on why we bond metallic conduits for a GEC is in the IEE Green Book
Doing and Requiring are two different beasts.....
 
Any conduit installed,when conductive, must have a means to trip the breaker if a current carrying conductor comes in contact with it. Emt will remain energized in the event of a fault unless bonded
 
Any conduit installed,when conductive, must have a means to trip the breaker if a current carrying conductor comes in contact with it. Emt will remain energized in the event of a fault unless bonded

However in most cases just a standard connector and lock nut do that job.


In the case of an EGC are required to do more bonding than that.
 
So would using a 3/4" bonding bushing be permissible in the panel alone or does it need to be at both ends of the conduit?

In general, it only needs to happen on one end, unless you are using it as the EGC.

In the special case of the GEC, it needs to happen on both ends. It doesn't necessarily need to be a bonding bushing, as a bonding U-bolt or other external pipe bonding clamp/strap could also suffice.
 