I would point to 250.96(A) which states:
Metal raceways, cable trays, cable armor, cable sheath, enclosures, frames, fittings, and other metal non?current-carrying parts that are to serve as grounding conductors, with or without the use of supplementary equipment grounding conductors, shall be effectively bonded where necessary to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed on them.
I've seen concentric KO's so mangled that there is one little tab barely hanging on to the enclosure or people who don't have a KO set and use the wrong size hole saw that gives a hole that the locknut tabs can barely grab.
If the connector is off plumb just a little then the shoulder and the locknut will not seat firmly on the wall of the enclosure.
I think those cases the conduit would not be effectively bonded as stated in the above section.