I was wirring up a ct service and noticed the cabinet was not bonded to service. I called inspector and he told me it doesnt have to be. I told him to look at 250.102. He still disagreed. I need a picture so he can see that it is wrong. The service is a 600amp parr. 500 alum. It comes from the transformer to a metal ct cabinet then the main all the conduits are PVC the sevice conductors pass threw donut cts the neutral just passes threw the cabinet no wires are terminated in cabinet(only my metering wires) Does anyone have a code picture of this instal so i can show this feller? thanks