Re: bonding CT can
Originally posted by michaelstanley:
What about exception #1 that says that the service switch can be on the supply side of the overcurrent device. If the transfer switch becomes the service switch and the overcurrent device is immediatly at the entrance of the conductors to the building, then that seems to meet exception #1.
The switch would have to be listed as "Service Equipment" 230.66
IMO having the switch outside and the overcurrent protection inside does not come close to the "immediately adjacent" requirement of 230.91.
As to the grounding conductor yes it can get complicated.
In as short as I can put it, on the supply side of the service disconnect the neutral is what you want to use to bond the metal enclosures, I am sure the neutral is already bonded to the CT can.
If the transfer switch does become the service disconnect you will bond the neutral to that enclosure also.
I would use PVC between the CT can and the service disconnect and you will not have to bond anything, the CT and the service disconnect will already be bonded to the neutral.
If you run metal pipe between these two enclosures you will have to bond the metal pipe.
Do not run a grounding conductor between the CT can and the service disconnect, that will only be a parallel conductor to the neutral, a violation of 310.4
If the transfer switch becomes the service disconnect you will need a grounding conductor from there to the old service.
In this case you would have to remove the main bonding jumper in the old service disconnect and move the grounding electrodes from the old service disconnect out to the new service disconnect.