Bonding DIN Rail

Status
Not open for further replies.

mic

Member
Does mounting zinc plated DIN rail to a painted steel backplate using self tapping screws provide an acceptable bond or is a jumper of some type required?

c
 
Re: Bonding DIN Rail

that is all i have ever used for the din rail, but the back plate needs an equipment ground, and a tech screw is not acceptable for this. the paint needs scraped, and you need to drill and tap a hole for the screw that holds the lug down.
 
Re: Bonding DIN Rail

does scraping the paint violate the requirement for corrosion protection on steel?
 
Re: Bonding DIN Rail

Originally posted by charlie b:
I may be DIM, but what's a DIN? :confused:
DIN is a standard I guess like NEMA.

Deutsches Institut f?r Normung
DIN

This is DIN Rail, you can get many components that snap onto DIN rail

mountingrail.jpg
 
Re: Bonding DIN Rail

"DIN rail" is a slang term for the mouning track commonly used with terminal blocks and other snap-on mounted devices in control panels.

A better description is 35mm DIN rail, for the most common style that looks like an upside down top hat.

There are actually three types of mounting rail:
DIN 1 - 15mm wide, symmetrical - looks like the old style terminal block mounting strips.
DIN 2 - 32mm wide, asymmetrical - looks like the letter G
DIN 3 - 35mm wide, symmetrical - 7.5mm deep is the most common size although many larger devices need the 15mm depth instead.

DIN rail also comes plated, galvanized, or bare in steel or aluminum and with or without prepunched mounting holes. The most common length is 2m for steel and 1m for aluminum. Some distributors even stock it in 3 and 6" precut lengths.
 
Re: Bonding DIN Rail

Originally posted by mic:
does scraping the paint violate the requirement for corrosion protection on steel?
I didnt know there was a requirement for corrosioin protection on steel. I saw it in the directions for a hoffman panel lug kit, and inspectors have always been looking for it.

Does taking a knockout out of an enclosure also chip off some paint?
 
Re: Bonding DIN Rail

I just learned something.. :)

Lets have a show of hands, how many here repaint a panel when they are done knocking out a hole, or coat the threads of conduit?
 
Re: Bonding DIN Rail

Every time ;) :p

I keep a wire brush that goes on the cordless drill to clean the paint off before I land a foot lug for EGC connections.

After bolting the lug in place once in a while I hit the area with gray primer but certainly not every time.
 
Re: Bonding DIN Rail

so you do it my way, iwire.

outside on the govt place i work, we use cold galvanized on the ends of strut, and conduit threads. inside we do nothing. we only repaint a panel when it really looks old ugly and dingy. and that is not for protection, it is for appearance.
 
Re: Bonding DIN Rail

Originally posted by mic:
Does mounting zinc plated DIN rail to a painted steel backplate using self tapping screws provide an acceptable bond or is a jumper of some type required?

c
I didn't know they made them zinc plated. I have only seem them chrome plated.

I seem to recall the steel DIN rails can be used for PE function but not the AL ones.
 
Re: Bonding DIN Rail

I think the correct term is zinc-bichromate not just zinc or chrome.
 
Re: Bonding DIN Rail

Originally posted by jbwhite:
Does taking a knockout out of an enclosure also chip off some paint?
Depends on how talented you are, how well the KO was punched, and how strong the metal is.

I'd be really impressed to see someone remove a KO but leave the paint! :D :D :D
 
Re: Bonding DIN Rail

The technical term used by the guys in our shop is "yellow rail". Not eloquent but very effective, even the new guys understand.

c
 
Re: Bonding DIN Rail

Petersonra wrote

"I seem to recall the steel DIN rails can be used for PE function but not the AL ones."

As I understand it, aluminium is liable to surface corrosion which would lead to contact resistance.

If anyone can provide more detailed information I would be very grateful.

Nigel Moore
Japan
 
Re: Bonding DIN Rail

" If anyone can provide more detailed information I would be very grateful."
I've never seen any specifications on this. DIN rail is a recognized, not listed product. UL 508 is likely to say maintain an effective ground fault current path.
I would contact a DIN rail manufacturer, such as Phoenix or Allen Bradley.
All the listed control panels I have worked in install the DIN rail with a pan head machine screw.
The terminal blocks typically are used with small wires and low ampacity circuits.
The solution is simple. The grounding terminal blocks mechnically clamp onto the rail. Run a wire from a grounding terminal block and terminate it to a properly intstalled bonding point.
 