Adamant321
- Atlanta, GA, USA
I'm working on a project and found an issue that concerns me. On the inside of this building there's a ground ring that runs along the entire wall about 10 feet up. It's bare stranded copper (I believe 4/0). The lightning protection down conductors are a braided mesh and connect to this ground ring, then the ground ring is tied into ground at a few points around the building. It seems the only thing that's connected to this ground ring is the lightning protection. Would we be allowed to tie equipment supplemental grounding to this ground ring? I'd imagine if the equipment is close enough to the ring then we would be required to bond to it to prevent sideflash. Is this correct?
I believe article 250.60 is what's throwing me off. Is this stating that the lightning protection system should be separate from the equipment ground system and then tied together at the grounding electrodes?
Thanks
Thanks