M mm Member Jul 24, 2004 #1 can someone tell what is the maximun size bonding conductor required by the nec to connect several electrodes
can someone tell what is the maximun size bonding conductor required by the nec to connect several electrodes
dereckbc Moderator Staff member Location Plano, TX Jul 24, 2004 #2 Re: bonding electrodes ? There is no maximum, only minimum.
iwire Moderator Staff member Location Massachusetts Jul 25, 2004 #3 Re: bonding electrodes ? I agree there is no maximum size allowed, there is a maximum required. mm Grab a code book and find this in Part III of Article 250.
Re: bonding electrodes ? I agree there is no maximum size allowed, there is a maximum required. mm Grab a code book and find this in Part III of Article 250.
H hurk27 Senior Member Location Portage, Indiana NEC: 2008 Jul 25, 2004 #4 Re: bonding electrodes ? Bob I agree there is no maximum size allowed, there is a maximum required. Click to expand... ? Grounding Electrode conductors are only required to be a minimum size, you are allowed to install a larger one. Or were you trying to say there is no maximum size, There is a minimum size required
Re: bonding electrodes ? Bob I agree there is no maximum size allowed, there is a maximum required. Click to expand... ? Grounding Electrode conductors are only required to be a minimum size, you are allowed to install a larger one. Or were you trying to say there is no maximum size, There is a minimum size required
iwire Moderator Staff member Location Massachusetts Jul 25, 2004 #5 Re: bonding electrodes ? Originally posted by hurk27: Or were you trying to say there is no maximum size, There is a minimum size required [/QB] Click to expand... Yes, I think.
Re: bonding electrodes ? Originally posted by hurk27: Or were you trying to say there is no maximum size, There is a minimum size required [/QB] Click to expand... Yes, I think.
H hurk27 Senior Member Location Portage, Indiana NEC: 2008 Jul 25, 2004 #6 Re: bonding electrodes ? I hate when that happens LOL