bonding EMT with electrode conductor

Status
Not open for further replies.
You have to bond both ends, see 250.64(E) for one article section that requires it.

Roger
 
stickboy1375 said:
FWIW, its usually much cheaper and easier to use a non-ferrous conduit for the GEC.

Other than no raceway at all, that is my preference.

Roger
 
stickboy1375 said:
I dont think I've ever used a raceway to be honest.

Unfortunately, a lot of commercial specs require it, even for SDS's in the protection of electrical closets/rooms for some stupid reason.

Roger
 
stickboy1375 said:
I dont think I've ever used a raceway to be honest.

That'd be a First ! :D

I was going to say:

Yes, Bond.
Remember that your connector is listed in most casing and should match your available flex! In most cases the flex with not have a additional copper ground interwoven your connector should match your availalbe flex choices. Till Roger spoke ...

If your consider that we bond at most circuit intersections, your changing from EMT to flex. Ok, which one. thus the bonding because you changed the dynamic's of the install.

Don't mind my moderated post ... I didn't read the code reference...
 
Last edited:
bonding EMT electrode conductor

bonding EMT electrode conductor

stickboy1375 said:
FWIW, its usually much cheaper and easier to use a non-ferrous conduit for the GEC.

I agree. I have failed many installations because metal conduit was not bonded at both ends.
 