Hello!
May I ask for your help? I am still a quite "young one" so there are tons of questions older and more experienced guys might know...
I am working on a site with another electrician who was called to do the underground feeder and meter pedestal at the pole.
Beside the pole (outdoors) he installed a meter socket and a fused disconnect switch. Here he bonded the Neutral to Ground with means of an adjacent 8' ground rod.
Then he ran 3 wires in SCH40 to the panelboard in the basement entering the building structure right beside the panelboard.
He asked me to seperate Grounds and Neutrals (ins. N-Bar)at the existing indoor panelboard and drive another ground rod at the house for the indoor panelboard (the way the wellpump is setup does not allow grounding there)
Since he is a superior (older and native)I did not express my doubts, but am I mistaken that:
A. You don't need a disconnect at the meter, since it is outdoors and the conductors enter right where the main panelboard is (IF YOU BURY IT DEEP ENOUGH, not even res. Driveway - plain garden)
B. If you don't need a disconnect, you don't need a ground rod out there, instead bonding N and G at the panelboard inside
C. If you have a disconnect, main panel becomes of course a subpanel, BUT THEN bonding is necessary with a bonding jumper (4th conductor)between disconnect and indoor panelboard, since we have a nonmetallic raceway (SCH40).
D. Anyway - shouldn't ALL groundrods, waterpipes, CATV, steel building structure, etc. be bonded together because of the equipotential (achieving the so called grounding system)?
Perhaps I am mad, I just don't understand it, or maybe it's because they still have the 1995 NEC here - is it a new approach since the NEC 2000?
When I cautiously asked, he said that the soil here has a really low resistance, and he didn't understand what I meant with equipotential.
So did I miss a point? I'd really like to know, so that I do it consciously the right way the next time.
Thanks for any replies!
May I ask for your help? I am still a quite "young one" so there are tons of questions older and more experienced guys might know...
I am working on a site with another electrician who was called to do the underground feeder and meter pedestal at the pole.
Beside the pole (outdoors) he installed a meter socket and a fused disconnect switch. Here he bonded the Neutral to Ground with means of an adjacent 8' ground rod.
Then he ran 3 wires in SCH40 to the panelboard in the basement entering the building structure right beside the panelboard.
He asked me to seperate Grounds and Neutrals (ins. N-Bar)at the existing indoor panelboard and drive another ground rod at the house for the indoor panelboard (the way the wellpump is setup does not allow grounding there)
Since he is a superior (older and native)I did not express my doubts, but am I mistaken that:
A. You don't need a disconnect at the meter, since it is outdoors and the conductors enter right where the main panelboard is (IF YOU BURY IT DEEP ENOUGH, not even res. Driveway - plain garden)
B. If you don't need a disconnect, you don't need a ground rod out there, instead bonding N and G at the panelboard inside
C. If you have a disconnect, main panel becomes of course a subpanel, BUT THEN bonding is necessary with a bonding jumper (4th conductor)between disconnect and indoor panelboard, since we have a nonmetallic raceway (SCH40).
D. Anyway - shouldn't ALL groundrods, waterpipes, CATV, steel building structure, etc. be bonded together because of the equipotential (achieving the so called grounding system)?
Perhaps I am mad, I just don't understand it, or maybe it's because they still have the 1995 NEC here - is it a new approach since the NEC 2000?
When I cautiously asked, he said that the soil here has a really low resistance, and he didn't understand what I meant with equipotential.
So did I miss a point? I'd really like to know, so that I do it consciously the right way the next time.
Thanks for any replies!