The scenario; the site has a new 4000A main service (MS). The main service is only a main breaker that feeds the 4000A distribution (MSA) at a remote location. The feeders for MSA are fifteen sets of (4) 400Kcmil and a 500 G in 4" conduits made up of PVC and OCAL risers. At the risers of each end there will be bonding bushings on the OCAL. The question is what size bonding conductor is to be used to bond all the bonding bushings?
Article 310.10(H)(6) refers to 250.102 for parallel bonding.
250.102(C)(2) describes the bonding jumper for the supply side. These conductors are protected by the 4000A breaker at MSA which will make them load side.
250.102(D) says to refer to table 250.122 which would be a 500Kcmil. This size is larger than the lay-in lugs on the bonding bushings and visually seems excessive. Am I adding this up correctly? If this is all correct how would you attach the 500Kcmil to the bonding bushing knowing that the lay-in lug doesn't have this size wire in wire range?
Article 310.10(H)(6) refers to 250.102 for parallel bonding.
250.102(C)(2) describes the bonding jumper for the supply side. These conductors are protected by the 4000A breaker at MSA which will make them load side.
250.102(D) says to refer to table 250.122 which would be a 500Kcmil. This size is larger than the lay-in lugs on the bonding bushings and visually seems excessive. Am I adding this up correctly? If this is all correct how would you attach the 500Kcmil to the bonding bushing knowing that the lay-in lug doesn't have this size wire in wire range?