2014 NEC art 250.102 (c) (2) states the following: where the ungrounded supply conductors are paralleled in two or more raceways or cables, and an individual supply-side bonding jumper is used for bonding these cables or raceways, the size of the supply side bonding jumper for EACH cable or raceway shall be based on and selected from table 250.102 (c) (1)
A single supply side bonding jumper installed for bonding two or more raceways or cables shall be sized in accordance with table 250.102 (c) (1)
in English, does the second part of the requirement mean that I can use one bonding jumper for all the cables as long as it is sized for the sum of the paralleled ungrounded conductors?
2014 NEC art 250.102 (c) (2) states the following: where the ungrounded supply conductors are paralleled in two or more raceways or cables, and an individual supply-side bonding jumper is used for bonding these cables or raceways, the size of the supply side bonding jumper for EACH cable or raceway shall be based on and selected from table 250.102 (c) (1)