wawireguy

Senior Member
I was wondering if have to treat a transformer as a service and bond the conduit to it with bonding bushings? Transformer is 120/208 with a 480 primary being fed from a distribution panel.

If you have rigid 90's stubbbing up through your floor that are being fed from PVC runs do you need bonding bushings on the conduits connecting to the panel?

If you do need to bond in either of these cases can you run a jumper from your bonding bushing to the can or do you have to loop your EGC through the bushing?

Appreciate the help!
 
Last edited:

raider1

Senior Member
Staff member
Location
Logan, Utah
There are no special bonding requirements for conduits feeding or comming from a transformer. The standard bonding requirements are all that apply.

Chris
 

wawireguy

Senior Member
I recall looking in the NEC before but not seeing anything specific for transformers. Guess I didn't miss that section!
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I recall looking in the NEC before but not seeing anything specific for transformers. Guess I didn't miss that section!

Nope you didn't miss anything.:)

I can definitely see why someone might feel that there would be enhanced bonding requirements for the secondary of a transformer.

Chris
 

wawireguy

Senior Member
How about this one guys. What if you bring the GEC to the transformer in your metallic conduit? I know if you brought the GEC into your service in metallic conduit you would have to bond both ends with bonding bushings, well at least if you ran it up the side of the building from say a couple of ground rods you would. I know I need to look this up but I got fish to catch : )
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
250.64(E) refers to bonding enclosures for bonding electrode conductors.
It does not specifically limit the requirement to services, so I would say the rule holds true for GEC on SDS also..
 

wawireguy

Senior Member
Hmm, just read 250.64(E) and it needs to be re-written for electricians. Luckily I have the hand book and it has a picture. Still wish I could interpret the engineer speak or whatever it is they wrote for that section.

Looks like you can use jumpers from your bushings instead of looping the GEC through the bushings.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Looks like you can use jumpers from your bushings instead of looping the GEC through the bushings.

Yes, you can use a bonding jumper from the bonding busing to the GEC if you want provided that the jumpers are sized the same as the GEC.

Chris
 