250.97 states "For circuits of over 250 volts to ground, the electrical continuity of metal raceways and cables with metal sheaths that contain any conductor other than service conductors shall be ensured by one or more of the methods specified for services in 250.92(B), except for (1)." exception "Where oversized,concentric, or eccentric knockouts are NOT encountered, or where a box or enclosure with concentric or eccentric knockouts is listed for the purpose, the following methods shall be permitted."
My question: I have a 120/208V 100A 1Ph sub panel (concentric Knockouts)which is fed with a 3/1 cu Feeder MC I am using a Regal 6244 insulated throat MC connector. The fitting is sized to fit into a standard 1 1/4" KO and is threaded an shouldered. I feel I neither need a Plastic bushing or a grounding bushing. I would love your input. Thanks
My question: I have a 120/208V 100A 1Ph sub panel (concentric Knockouts)which is fed with a 3/1 cu Feeder MC I am using a Regal 6244 insulated throat MC connector. The fitting is sized to fit into a standard 1 1/4" KO and is threaded an shouldered. I feel I neither need a Plastic bushing or a grounding bushing. I would love your input. Thanks