Cavie
Senior Member
- Location
- SW Florida
I seem to remember reading about bonding the interior metal wall framing members but can't to find it. Any help??
Do people use plastic boxes on metal studs? I suppose you could with certain types, but I've never seen it done with my own two eyes.Davis9 said:What if you use plastic boxes?
That sounds like an inspector that never saw metal studs before.cloudymacleod said:mdskunk, i did a job that had metal studding that we used plastic boxs on in a big residential job. then we had to bond the studs.the inspector insisted we bond the studs like a frigan pool with a #8.
don_resqcapt19 said:Steel studs are not required to be bonded by the NEC as they are not "exposed structural metal". 250.104(C).
Don
Yes it would be the AHJ call based on this code section. It is my opinion that while it is possible that the metal studs would be come energized, it is not likely.Would 250.4(A)(4) apply? Or is this an inspectors call.
tom baker said:Mike Holt has a graphic that shows metal studs, plastic boxes and one metal box that does the bonding
I have heard based on a death in FL that the 2008 NEC may require bonding of metal studs.
Section 2704:
Bonding Metal Framing Members: Metal framing members. Metal framing members shall be bonded to the equipment grounding conductor for the circuit that may energize the framing and be sized in accordance with the National Electric Code Table 250.122. For the purpose of this section, a grounded metal outlet box attached to the framing shall be permitted.