Is it required to bond the gas pipe in a single building residence?
Article 250.52 (7)
(B)Electrodes Not Permitted for Grounding
(1) Metal underground gas piping system.
Article 250.104
(B) Other Metal Piping
Where installed in or attached to a building or structure, metal piping systems, including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure...
[ January 17, 2006, 12:07 PM: Message edited by: powerqualitycc ]
Article 250.52 (7)
(B)Electrodes Not Permitted for Grounding
(1) Metal underground gas piping system.
Article 250.104
(B) Other Metal Piping
Where installed in or attached to a building or structure, metal piping systems, including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure...