I'm looking at 250.104 (3)(B) and I'm unclear on one thing. The only gas appliance in this house is a gas range. This gas pipe was installed after I roughed in the house and I did not know about it until I showed up to do the trim. I had a junction behind the range for a bunch of under cabinet lights and there was power in it so I just wired a plug on it instead of blanking it off. It is on a 15 amp lighting circuit. So my question is what size wire do I have to use to bond the pipe? I'm thinking that this would be the only circuit that is likely to energize the pipe. Can I just bond it with a 14 guage wire??
edit.
Found my answer in my states local rules
104(B) Bonding ? other metal piping.
(10) For flexible metal gas piping, installed new or extended from an existing rigid metal piping system, either:
(a) Provide a copy of the manufacturer?s bonding instructions to the inspector at the time of inspection and
follow those instructions; or
(b) The bonding conductor for the gas system must:
(i) Must be a minimum 6 AWG copper; and (ii) Terminate at:
(A) An accessible location at the gas meter end of the gas piping system on either a solid iron gas pipe or a cast flexible gas piping fitting using a listed grounding connector; and
(B) Either the service equipment enclosure, service grounding electrode conductor or electrode, or neutral conductor bus in the service enclosure.
edit.