sfav8r
Senior Member
- Location
- San Francisco Bay Area
Here in San Francisco we are required to bond the gas pipe withing 5' of where it enters the premises. We just did a job in another jurisdiction and bonded the gas pipes as we always do. The inspector called us on the installation stating that the gas pipe must be bonded at the hot water heaters. 210.104(B) states that the gas pipes must be bonded to "service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to one or more of the grounding electrodes." How does bonding the gas pipe at the hot water heater meet this requirement? Even if it did meet the requirement, where in the code does it say we can't bond it the way we did? Also, he is requiring us to remove the hot/cold bond because we used #6 stranded and he says it has to be solid. I thought that requirement only applied to hot tub bonding. It's not a big deal to correct this, I just resent having to make correction that I don't believe are necessary. You'd think I'd be in a better mood after last nights Giants game!