ga1212ett
Member
- Location
- california
hello,
what NEC article should i be using to size ground wires for ground bushings bonding to equipment. (required per job specs) ,equipment is an mcc fed from a utility meter box, with a main disconnect between the meter and MCC. They just specify to bond the bushings to ground bus without actual sizing requirements listed.
More information, the Main is 1600A breaker with 6 sets of parallel 350mcm copper conductors per phase and 250 mcm ground per set. 480v, no neutral.
the conduit is pvc underground with pvc coated rigid conduit risers.
the MCC is open bottom and will not have continuity with the risers without this bonding conductor.
Thanks for your time.
what NEC article should i be using to size ground wires for ground bushings bonding to equipment. (required per job specs) ,equipment is an mcc fed from a utility meter box, with a main disconnect between the meter and MCC. They just specify to bond the bushings to ground bus without actual sizing requirements listed.
More information, the Main is 1600A breaker with 6 sets of parallel 350mcm copper conductors per phase and 250 mcm ground per set. 480v, no neutral.
the conduit is pvc underground with pvc coated rigid conduit risers.
the MCC is open bottom and will not have continuity with the risers without this bonding conductor.
Thanks for your time.