The drawing below covers a ground to neutral bonding application. The question is "Can/should the earth ground be connected to the breaker panel neutral bar? What NEC code section has the answer?"
https://drive.google.com/file/d/1K8IxzwcTbN3NBCgziyqvUiI-HLlSK2i6/view?usp=sharing
If the drawing cannot be accessed, I will try to explain the issue. Grid power (480VAC 3Φ) feeds a UPS, then UPS power feeds a 480VAC 1Φ to 240/120VAC 1Φ transformer. The earth ground wire is connected to the center tapped neutral at the transformer. The transformer feeds a 240/120VAC 1Φ breaker panel. Breakers (120VAC 1Φ) feed 20A receptacles that power a crane control system. Earth ground is connected to the neutral bus bar inside the breaker panel. There is no ground rod at the transformer. Earth ground originates at the grid power connection.
https://drive.google.com/file/d/1K8IxzwcTbN3NBCgziyqvUiI-HLlSK2i6/view?usp=sharing
If the drawing cannot be accessed, I will try to explain the issue. Grid power (480VAC 3Φ) feeds a UPS, then UPS power feeds a 480VAC 1Φ to 240/120VAC 1Φ transformer. The earth ground wire is connected to the center tapped neutral at the transformer. The transformer feeds a 240/120VAC 1Φ breaker panel. Breakers (120VAC 1Φ) feed 20A receptacles that power a crane control system. Earth ground is connected to the neutral bus bar inside the breaker panel. There is no ground rod at the transformer. Earth ground originates at the grid power connection.