I have a couple grounding related questions related to the attached drawing of my service entrance (which has a very typical configuration).
1. It is my understanding that the neutral should be isolated in the meter box (not physically connected to the grounded enclosure), because if the neutral and ground were tied together at the meter box as well as the main panel, loop currents would be created. is this correct?
2. Should the meter box be grounded via the grounding block that is mounted on the enclosure? If so, to where? Should it go to the grounding rods associated with the main service panel? Should it go to the grounding lugs in the main panel? If it should not be grounded, why not? The meter box is mounted to a steel building, so it is essentially being grounded indirectly through the steel of the steel building to the main panel enclosure, which is grounded through the grounding rods.
3. The meter box and the main panel are mounted to the same steel building. So they are indirectly grounded together.
4. Is there a possibility of loop currents because the steel building is grounded itself, and the grounding rods are grounded. So each would be at a slightly different ground potential level, which would create loop currents? Is this correct?
5. Should the steel building structure be grounded to the service panel grounding rods?
I have done many service entrances over the years, but this was the first that involved mounting on a steel building, which made me question some of these items. Any help would be appreciated!
Greg
1. It is my understanding that the neutral should be isolated in the meter box (not physically connected to the grounded enclosure), because if the neutral and ground were tied together at the meter box as well as the main panel, loop currents would be created. is this correct?
2. Should the meter box be grounded via the grounding block that is mounted on the enclosure? If so, to where? Should it go to the grounding rods associated with the main service panel? Should it go to the grounding lugs in the main panel? If it should not be grounded, why not? The meter box is mounted to a steel building, so it is essentially being grounded indirectly through the steel of the steel building to the main panel enclosure, which is grounded through the grounding rods.
3. The meter box and the main panel are mounted to the same steel building. So they are indirectly grounded together.
4. Is there a possibility of loop currents because the steel building is grounded itself, and the grounding rods are grounded. So each would be at a slightly different ground potential level, which would create loop currents? Is this correct?
5. Should the steel building structure be grounded to the service panel grounding rods?
I have done many service entrances over the years, but this was the first that involved mounting on a steel building, which made me question some of these items. Any help would be appreciated!
Greg