I’m a bit confused on how to correctly do all this and neutral sizing seems contradictory depending on the author.
I’m installing a 400amp 480V Panel from a CT can which comes from a new utility transformer that’s yet to be installed. Utility wanted 2 parallel runs of 500kcmil copper for 800amps at the can. Pretty unlikely we’ll add anything else to the can. Inspector says this requires a neutral, any issues with sizing that at a parallel 1/0?
I drove 2 ground rods for our transformer, since the 480v is considered a service he wants the ground rod wire (EGC) installed at the 480v panel.
What do I now do with the step-down 112.5 kva transformer I’m installing? Neutral goes to X0 already and lands on neutral bar in my 208 panelScribbled one-line
I’m installing a 400amp 480V Panel from a CT can which comes from a new utility transformer that’s yet to be installed. Utility wanted 2 parallel runs of 500kcmil copper for 800amps at the can. Pretty unlikely we’ll add anything else to the can. Inspector says this requires a neutral, any issues with sizing that at a parallel 1/0?
I drove 2 ground rods for our transformer, since the 480v is considered a service he wants the ground rod wire (EGC) installed at the 480v panel.
What do I now do with the step-down 112.5 kva transformer I’m installing? Neutral goes to X0 already and lands on neutral bar in my 208 panelScribbled one-line