What is your opinion on this code issue:
*1600A 3ph 480/277 service with CEE
*Structural steel in a IIIB building is bonded near the electrical room.
*Water service & metallic piping is far away from the electrical room.
*Contractor uses a bonding jumper from the bar joist to the metal water pipe up in the ceiling.
Is this a violation?
I feel as though this is a violation of 250.104(A)(1)
There may be electrical continuity which would be common sense but it does not meet the requirements of the above reference.
What say you????????