(D) Other Metal. Where installed in or attached to a building or structure, metal objects that are likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.
Substantiation: It is evident that code understands the fact that bonding isolated metal is an enhancement in safety. This can be verified by referring to the fine print notes of 250.104(B) and 250.116. Because there are, in fact, documented deaths that have occurred because of the lack of bonding of such things as nonstructural metal wall framing and ducting systems, this concept should be a requirement, and not just a suggestion in the form of a fine print note. This proposal uses the existing text of 250.104(B) in an effort to provide consistent code language between the two subsections.
A companion proposal to delete the FPN to 250.116 will be submitted for
correlating purposes.
Panel Meeting Action: Reject
Panel Statement: The terms ?other metal? and ?metal objects? are vague and unenforceable as used in this context.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15