If there is 10 feet of copper coming into a house and from there it is plastic water lines, do you still have to bond the pump to the 6 inches of copper lines that came with the tub?
Code #----bphgravity said:Yes.
The pipe would already be bonded for other reasons.That 6 inches at faucet will do nothingmarinesgt0411 said:680.74 All metal piping systems, ...
sparkadaddy said:If there is 10 feet of copper coming into a house and from there it is plastic water lines, do you still have to bond the pump to the 6 inches of copper lines that came with the tub?
680.74 Bonding. All metal piping systems and all grounded metal parts in contact with the circulating water shall be bonded together using a copper bonding jumper, insulated, covered or bare, not smaller than 8 AWG solid.
marinesgt0411 said:it goes on to say that all metal attached to the tub will be bonded.
do not shoot the messenger
sparkadaddy said:the 6 inches of pipe is right under the faucets from there it is plastic. The whole house is plastic except where the water service enters house is copper.