We have a 2500Kva Padmount Transformer. Primary 12,470, with a 480/277v secondary. The "service entrance" conductors consisted of 8 paralleled 500MCM copper conductors with a full size neutral going to a 3000Amp Main Breaker, with a "number" of "fusible" branch feeders. We established the "bond" in the switchboard at the neutral bar, by running a seperate 3/0 copper to EACH of the following points. 1. Incoming water pipe. 2. To the Building Steel. 3. Rebar steel in the footer of the building.
My question is this: In the 2500kva transformer "hanging" from the Neutral Bushing is a "strap" with a hole in the end of the strap. Since we are "bonded" in the SWBD at the Neutral don't we let this strap in the transformer stay in the "disconnected" position?