This is a 2 part Bonding in Class II Div 1 environments question.
1st - When using LFMC (less than 6') to connect to equipment as allowed per 502.10(A)2 & (B)2, and there is an equipment grounding conductor (EGC) installed within the raceway, is there a need to install and external equipment bonding jumper? I believe that 502.30(B) requires a bonding jumper per 250.102 and that 250.102(E)(1) allows for the bonding jumper to be installed inside the raceway. Can the EGC installed within raceway serve as both EGC and bonding jumper?
2nd - 250.100 requires bonding of raceways per 250.92(B)(2)-(B)(4). 250.92(B)(3) lists threadless coupling and connectors if made tight for metal raceways and metal-clad cables. Would this apply to LFMC connectors? I associate threadless couplings and connectors with either compression or set screw fittings for Rigid or EMT. Would this apply to LFMC? For example, if LFMC connector was used to connect to and enclosure (without concentric ko's) outside of Class II Div 1 areas, would this be a sufficient connection for electrical continuity or would another listed device (bonding bushing or locknut) per 250.92(B)(4) be required?
Thank you for your replies.
1st - When using LFMC (less than 6') to connect to equipment as allowed per 502.10(A)2 & (B)2, and there is an equipment grounding conductor (EGC) installed within the raceway, is there a need to install and external equipment bonding jumper? I believe that 502.30(B) requires a bonding jumper per 250.102 and that 250.102(E)(1) allows for the bonding jumper to be installed inside the raceway. Can the EGC installed within raceway serve as both EGC and bonding jumper?
2nd - 250.100 requires bonding of raceways per 250.92(B)(2)-(B)(4). 250.92(B)(3) lists threadless coupling and connectors if made tight for metal raceways and metal-clad cables. Would this apply to LFMC connectors? I associate threadless couplings and connectors with either compression or set screw fittings for Rigid or EMT. Would this apply to LFMC? For example, if LFMC connector was used to connect to and enclosure (without concentric ko's) outside of Class II Div 1 areas, would this be a sufficient connection for electrical continuity or would another listed device (bonding bushing or locknut) per 250.92(B)(4) be required?
Thank you for your replies.