This is an old house plumbed with copper water lines. Inspector came in to inspect upgrade and remodel in one part of the house. He found pre-existing work he has cited. Inspector wants me to bond sections of copper water pipe around a section that was previously repaired with PEX. This section is Upstream from the bonding jumper between the panel and the connection to the cold water pipe. Hot and Cold lines are bonded together thru several substantial brass mixing valves used in the existing plumbing system. Pex was used to repair a leaking section on the cold water line in the basement where it goes up an interior wall to the second floor bath. Upstream of this Pex repair is only this bath. The bath circuit is protected by a GFCI. Mike makes a note in his book "Understanding the NEC" under this section as follows: "Bonding is not required for isolated sections of metal water pipe connected to a non-metallic water piping system". I have researched this code section and can't find much additional info on the exception Mike references. I realize it may be easiest to just install a bonding jumper, properly sized. I am curious about the exception Mike mentioned vs the inspector's interpretation as I am apt to encounter this again in the course of my property management business. Appreciate your insights. Thanks