isupowerplant
Member
- Location
- Ames, Iowa
Installing a grounding electrode at a building's incoming water service per NEC 250.52(A)(1) and the plan was to jumper across water meter. However, contractor asked if the jumper was necessary due to the bypass pipe below the section with the meter. I am of the opinion that the jumper is not needed, assuming all the piping is mechanically continuous. See picture with grounding electrode conductor attached to the exterior side of the meter. Thank you for your review and opinion.