Have a 400 amp disconnect that has small bus bar that jumpers to the frame with a green ground screw from the neutral terminal . ( System Bonding Jumper ) The grounding electrode conductor to building steel is also tied to the neutral lug . There is a ground lug on the bottom of the cabinet that the equipment grounding conductors tie-in to . Engineer says that because drawings show what looks like a wiring that goes directly to the ground bar ( System Bonding Jumper ) there needs to be a wire to the ground bar . Its already grounded thru the cabinet and the existing system bonding jumper . Is this not correct as it is ?