borracho.del.pueblo
New User
- Location
- TN
- Occupation
- Electrical Supply
I'm being told that bonding jumpers are unnecessary for the cable tray I'm quoting. - Legrand Cablofil 09-6A12C-S144-36 (Cross sectional area of 1in2 ) The table at NEC article 392.60 specifies a 1200A maximum for that area of aluminum tray. This maximum ampere rating appears to be the maximum of any individual breaker, fuse, or protective relay that is protecting a circuit run from the tray. After asking around a bit it seems that some run a separate EGC and bond each piece of tray/connectors using something similar to a Eaton 9A-2130. Would you guys run a separate EGC or use the tray as EGC as long as it is within limitations?