I want to make sure I am applying article 250 correctly here. I have an industrial control panel fed from a 200 amp 3 phase straight 480 v bus drop. Inside that panel I have a branch circuit supplying the primary of a drive isolation transformer mounted to the floor adjacent to this panel. The 480Y/277 (solidly grounded) volt 3 phase secondary feeds back into the same panel and is then distributed to various VFDs and other motor circuits. As there are no 277 volt loads, no current carrying conductor is brought back to the panel with the phase conductors.
Am I correct in understanding 250.30 (A) in that I should take a system bonding jumper (identified with the color green), sized according to 250.28(D) from the X0 terminal in the transformer, run it along with the secondary phase conductors and connect it to the main ground bus in the control panel?
If this is correct, can I then bond the transformer enclosure to that X0 lug also?