- Location
- Sacramento, CA
We have a pump control panel that was delivered to us with the Main Bonding Jumper terminated on the line side of the Neutral Disconnect link. NEC 230.75 states that disconnecting means shall be required to disconnect the Service Grounded Conductor from the premise wiring. In this installation when the Neutral Disconnect is pulled and the Main Breaker is opened all premise wiring is not disconnected from the Service Conductors. The grounding system is still connected. Does this meet the NEC intent?