Designer371141
Member
Our lead engineer is directing us to remove the bonding jumper at our generator and install conductors from the center tap of the wye connected generator to the first disconnecting means in a different location, once they are there the bonding jumper is to be installed between the equipment ground and the neutral bus. Article 250.30 (2) indicates that the bonding jumper shall be installed at the source when the source and the disconnect are in different locations. There would be no gain in doing this as he has designed the system, only additional cost because of the fourth current carrying conductor in with the feeders, and de-rating. The conductor size has to also be increased.
Am I understanding Article 250 correctly
Am I understanding Article 250 correctly