I recently did a service change on a ranch to include an additional house. It is a 120/240 single phase service. The service conductors entering the gutter from the service drop are three copper 500 KCmil. I have three disconnects tapped off these conductors. A 50 amp for a well, a 150 amp for one house, and a 200 amp for another house.
What size bonding jumper do I need to bond the gutter to the three disconnects? If I understand it correctly, 250.102 (C)(1) refers me to Table 250.66 for a bonding jumper size of 1/0 based on the 500 KCmil ungrounded service conductor. Do I understand this correctly? Thanks