Re: Bonding Jumper Size
IMHO the definition of grounding electrode conductor includes these bonding jumpers between electrodes. By bonding two electrodes together you are connecting a grounding electrode to the grounded conductor.
for example, if you run a GEC to the metal frame of the building next to the service, and at the opposite corner of the structure the water enters, if you choose to run a conductor between metal frame and water at this point, is it a GEC or is it a bonding jumper. This conductor could be very short, maybe 3' or more. There is no doubt that it is bonding two electrodes together. I also believe it is connecting the metal underground water pipe to the grounded conductor and the equipment grounding conductor (per definition 100). Therefore, it is a GEC and must follow all sections that apply.
Fred